SERVICE DISRUPTION NOTICE (SDN)
NOTICE TIME ZONE Brisbane UTC +10
STATUS (Open/Closed) Closed
CAUSED BY A 3RD PARTY? No
IF YES, NAME OF 3RD PARTY
START DATE 20250626
START TIME (HHMM) 0703
ESTIMATED TIME TO RESOLUTION UNKNOWN
END DATE 20250627
END TIME (HHMM) 1508
TOTAL DURATION Approx 8 Hours
ESTIMATED DOWN TIME FOR AFFECTED USERS 8 Hours
XCRM TICKET NUMBER Not Applicable
BRAND XNET
PRIORITY P1
CLIENTS AFFECTED BROOKFIELD 4069 Clients
DESCRIPTION OF INCIDENT Internet connection outage caused by failed router.
EVENT TIMELINE
Thursday 26th June 2025
0703 XSTRA became aware of outage from PRTG monitoring alerts. Determined failed router. Technician is on route to investigate root cause.
1500 XSTRA completed works to replace faulty router at the Kenmore Data Center – Tested OK
RECOVERY & RESOLUTION Replaced faulty hardware
ROOT CAUSE Failed router in the Kenmore data center
CORRECTIVE & PREVENTATIVE MEASURES None – all hardware is subject to eventual failure. Given the nature of the traffic passing through the router, the level of importance did not justify additional investment in redundancy. However, we had appropriate contingencies in place, including spare hardware and up-to-date configuration backups, which enabled a prompt and effective replacement.