NOTICE TIME ZONE |
Brisbane UTC +10 |
STATUS (Open/Closed) |
Closed |
INCIDENT CAUSED BY A 3RD PARTY? |
No |
IF YES, NAME OF 3RD PARTY |
N/A |
INCIDENT START DATE |
20230829 |
INCIDENT START TIME (HH:MM) |
15:23 |
ESTIMATED TIME TO RESOLUTION |
|
INCIDENT END DATE |
20230829 |
INCIDENT END TIME (HH:MM) |
16:12 |
INCIDENT TOTAL DURATION |
49 minutes |
XCRM TICKET NUMBER |
Not Applicable |
BRAND |
XNET |
PRIORITY |
P1 |
CLIENTS AFFECTED |
All Clients |
DESCRIPTION OF INCIDENT |
All Services |
EVENT TIMELINE |
|
|
Tuesday 29th August 2023 |
15:23 |
XSTRA Monitoring indicates all communications at NEXDC B2 are down |
15:35 |
Technician has been despatched to NEXTDC B2 site – ETA 25 minutes |
15:55 |
Hardware determined at fault |
16:10 |
Hardware replaced |
RECOVERY & RESOLUTION |
Hardware replaced |
ROOT CAUSE |
Mikrotik CRS 1036 in boot loop |
CORRECTIVE & PREVENTATIVE MEASURES |
N/A – hardware will fail at some point – replacement hardware was ready and pre-configured for efficient and timely swap out |