NOTICE TIME ZONE |
Brisbane GMT+10 |
STATUS (Open/Closed) |
Closed |
INCIDENT START DATE |
20200831 |
INCIDENT START TIME (HH:MM) |
Approx: 08:30 |
ESTIMATED TIME TO RESOLUTION |
N/A |
INCIDENT END DATE |
20200831 |
INCIDENT END TIME (HH:MM) |
Approx: 09:41 |
OUTAGE DURATION |
Approx. |
INCIDENT CAUSED BY A 3RD PARTY? |
Yes |
IF YES, NAME OF 3RD PARTY |
TPG/AAPT – VIC POWER |
XCRM TICKET NUMBER |
12881 |
BRAND |
XNET |
PRIORITY |
P3 – Medium |
CUSTOMERS AFFECTED |
X40 |
SITES AFFECTED |
C-40-7 |
DESCRIPTION OF INCIDENT |
C-40-7 office has no Internet access via fiber. |
PRIMARY IMPACT EFFECT |
Users may have issues accessing the Internet |
SECONDARY IMPACT EFFECT |
Out of band access for XSTRA to monitor devices via PRTG is limited |
EVENT TIMELINE |
|
|
MONDAY 31ST AUGUST 2020 |
08:30 |
XSTRA’s monitoring system, PRTG, advise Internet at C-40-7 was down |
08:41 |
MS (XSTRA) escalated to LB (XSTRA) |
08:45 |
LB (XSTRA) confirmed service is offline, checked known outage in area |
08:59 |
LB (XSTRA) made contact via teams with Darren and Randolph to identify if known outage |
09:00 |
LB (XSTRA) made contact with upstream carrier to lodge fault |
09:05 |
LB (XSTRA) confirmed carrier outage as gateway for service also not responding |
09:40 |
LB (XSTRA) confirmed services restored |
09:42 |
DH (JAG) arrived onsite and confirmed services returned |
RECOVERY & RESOLUTION |
|
ROOT CAUSE |
|
|
Fault linked to upstream carrier power outage at flinders street |
CORRECTIVE & PREVENTATIVE MEASURES |
|
|
Re-establish 4G service since disconnection of 2nd fibre service |
RESIDUAL EFFECT |
None |
Feedback
Thanks for your feedback.
Post your comment on this topic.